Just reading back on this thread, is the earth connection to the chassis not for bonding extraneous metal parts ? I don't think it's intended as an earth for your EHU. The site should be supplying you an earth via a rod ( TT system which will be tested regularly via an approved electrician. The 30mA RCD will note any imbalance between live conductors. A TT system has to have RCD protection as the resistance of the earth path can be unstable and not normally low enough to trip an MCB under short For an MCB to trip the loop impedance must be low enough as in accordance with BS7671. The MCB in a TT system is only there for overload protection as the it unlikely to trip in the event of a fault within 0.4 or 5 seconds hece the RCD. Noting that in accordance with amendment 2 that only Type A RCD'S can be used where DC voltage is present.
It also states the that the overload protection must isolate All live conductors, meaning double pole MCBS.