I am just about to install a Victron Multiplus 12/500/20 500VA inverter charger under my drivers seat and have been provided with a kit from a supplier that includes 2 consumer units, 1 for the incoming supply between the EHU and the Multiplus, and 1 for the outgoing supply between the Multiplus and 240V sockets in the back of the van.
My question is about the ratings of the MCBs & RCDs pre-installed in the consumer units and would welcome your opinions and advice.
The incoming CU is a 1way unit with 25A RCD and a single 10A MCB. The outgoing CU is a 2way unit with the same RCD, 1x10A MCB and 1x6A MCB. Both CUs are the same type with Gacia double pole MCBs/RCDs.
I was told its ok to use these CUs without changing the MCBs/RCDs but in my limited knowledge its bad practice to have:
1. RCDs of the same rating on the first and second CUs
2. An MCB of a lower rating (10A) in the first CU than the combined MCBs rating (16A) in the second CU
It makes sense to me to keep the MCB and RCD sizes in the second CU for the outgoing circuits but what rating MCB and RCD should I use in the first CU?
Cable size throughout is 2.5mm 3core artic blue.
Thanks!
Edit: peak power output of the inverter is 900W, continuous power output is 430W so maybe the MCBs in the second CU are rated too high in total anyway?
My question is about the ratings of the MCBs & RCDs pre-installed in the consumer units and would welcome your opinions and advice.
The incoming CU is a 1way unit with 25A RCD and a single 10A MCB. The outgoing CU is a 2way unit with the same RCD, 1x10A MCB and 1x6A MCB. Both CUs are the same type with Gacia double pole MCBs/RCDs.
I was told its ok to use these CUs without changing the MCBs/RCDs but in my limited knowledge its bad practice to have:
1. RCDs of the same rating on the first and second CUs
2. An MCB of a lower rating (10A) in the first CU than the combined MCBs rating (16A) in the second CU
It makes sense to me to keep the MCB and RCD sizes in the second CU for the outgoing circuits but what rating MCB and RCD should I use in the first CU?
Cable size throughout is 2.5mm 3core artic blue.
Thanks!
Edit: peak power output of the inverter is 900W, continuous power output is 430W so maybe the MCBs in the second CU are rated too high in total anyway?