Both methods are as simple as you can get, its just two wires. Cheaper? , no cos they come with cables attached, nothing else to buy. Series can be more expensive as you need to buy a HV controller. Agree high V low A is more efficient. Third point, disagree, at 13v a panel is almost inactive & wont be supplying any worthwhile current.Parkedinparadise said:Wiring Solar Panels In Series
- No need for fuses and wiring is simpler and cheaper.
- Higher voltage rather than amperage means the system is a more efficient.
- In certain light conditions, series is better. Overcast days or low light situations benefit from series wiring. If panels are only getting enough sun to output 13V, then two panels in parallel won’t be outputting enough voltage to properly charge the batteries at 13.8V. If you’re wiring in series, you’re getting 26V which can be stepped down for a proper charge.
Point 1 is a gross oversimplification as a decent PWM controller will be switch mode and wont 'lose anything above 13.8v', they simply lack mpp tracking. Doesnt apply to your Ctek anyway. 2nd point agree. 3rd point solar panels are inherently resistive compared to say a battery, they are incapable of massive currents and dumping into a short would be harmless. Thats what the Isc spec means. Cells are connected in parallel (and parallel bunches in series) within a panel anyway.Parkedinparadise said:Wiring Solar Panels In Parallel
- Most PWM controllers need parallel wiring. These charge controllers are only rated to a slightly higher input voltage than the battery bank. So if you have two 18V panels and wire in series to put in 36V of power into a PWM controller, you’re loosing anything above the 13.8V that’s going into your batteries.
- In certain shade conditions parallel is better. If one panel is shaded and the other isn’t, you aren’t loosing as much power because you’re still getting the full voltage from the panel in the sun.
- Parallel solar needs bigger wiring, fuses, and combiners. Each panel must be fused at the combiner junction in case one shorts out. The wiring must be bigger as you are increasing amps.
...and with series wiring, if one is shaded the entire array goes down, not just one panel as is the case with parallel.Parkedinparadise said:Shade
Another big thing to know about panels is that most solar tech is very sensitive to shade. Each of the little squares on your panels are wired in a way that if one of them is shaded, the whole row can’t produce energy. Because of this, you can reduce your energy produced by up to 90% if a certain 10% of the panel is covered.
I fancy a custom 4-panel series-parallel into my Victron (4 x 100w, 40v 200w) if this was available as a large single panel on the roof with a single pair of cables off the roof, that would be my ideal.
Yep one large panel is so much neater... at 400w they're usually rigids or multiple flexis though.
You'd think SCA, Reimo, Skyline, Austops etc poptop manufacturers would have cottoned on to this...
No probs!@Phil_G many thanks for your input.
Why? its only over the Ctek voltage if you go series.Tricky decision! Though I'm wanting to get it right first time! Leaning toward parallel now though to be honest because of the shading issue as you say. Though I would then need a separate solar controller.
No fridge will take 50 amps. Maybe 5, usually 3-4 for a Waiko/Dometic and thats only when the compressor is running. With minimal door-opening, my Dometic runs about 6:1 off/on duty cycle so over 24hrs maybe 16-20Ah ish.On the plus side I've worked out that if we have a fridge my power draw will be c. 50A per day
200 is a nice size. It not about peak power when its sunny, larger panels are preferable for getting some charge under poor conditions...so will need 200W of solar to replenish in high summer.
It depends how the 4 panels are wired. Maximum resilience is with all 4 in parallel. If you do them series-parallel,Would 4 panels fair better in the instance that one was fouled with bird poo, in that three of the four would continue to harness energy? Or has partial-blockages of solar panels been overcome?
be careful with your units, I know it sounds pedantic but its important, presumably you mean 45Ah not 45AId got it to 45A per day